Top > INSTALLATION > Connecting Electricity > Electrical Requirements

Electrical Requirements

This appliance must be installed and grounded on a branch circuit by a qualified technician in accordance with the National Electrical code ANSI/NFPA NO. 70 - latest edition.

All wiring should conform to local and NEC codes. This range requires a single-phase, 3 wire, AC 120/208 V or 120/240 V 60 Hz electrical system. Use only a 3-conductor or a 4-conductor UL - listed range cord with closed-loop terminals, open-end spade lugs with upturned ends or similar termination. Do not install the power cord without a strain relief.

A range cord rated at 40 amps with 120/240 V minimum range is required.

If a 50 amp range cord is used, it should be marked for use with 1 3/8" diameter connection openings. This appliance may be connected by means of a conduit or power cord. If a conduit is being used, refer to "3-Wire Connection: Conduit" or "4-Wire Connection: Conduit" sections.

Warning
  • Allow 2 to 3 ft (61.0 cm to 91.4 cm) of slack in the line so that the range can be moved if servicing is ever necessary.

  • The power supply cord and plug should not be modified. If the plug will not fit the outlet, have a proper outlet installed by a qualified electrician.

  • Using an extension cord to connect the power is prohibited. Connect the power cord and plug directly.

  • Electrical ground is required on this appliance.

  • Make sure that the power cord is not pinched by the range or heavy objects. Failure to do so can result in serious burns or electrical shock.

Specified Power Cord Kit Rating

Case 1
  • Voltage: 120/240 volts (3-wire)

  • Range rating: 8,750 W - 16,500 W

  • Specified rating of power supply-cord kit, amperes: 40 A or 50 A

  • Diameter (inches) of range connection opening

    • Power cord: 1 3/8"

    • Conduit: 1 1/8"

Case 2
  • Voltage: 120/240 volts (3-wire)

  • Range rating: 16,501 W - 22,500 W

  • Specified rating of power supply-cord kit, amperes: 50 A

  • Diameter (inches) of range connection opening

    • Power cord: 1 3/4"

    • Conduit: 1 3/8"

Case 3
  • Voltage: 120/208 volts (3-wire)

  • Range rating: 7,801 W- 12,500 W

  • Specified rating of power supply-cord kit, amperes: 40 A or 50 A

  • Diameter (inches) of range connection opening

    • Power cord: 1 3/8"

    • Conduit: 1 1/8"

Case 4
  • Voltage: 120/208 volts (3-wire)

  • Range rating: 12,501 W - 18,500 W

  • Specified rating of power supply-cord kit, amperes: 50 A

  • Diameter (inches) of range connection opening

    • Power cord: 1 3/4"

    • Conduit: 1 3/8"

3, 4 - Wire Electrical Wall Receptacle

4 Wire receptacle (14-50R)

3 Wire receptacle (10-50R)